Hi
all,
Robert
has it pretty well nailed down in his comments; however, some clarifications
could be helpful to those following this discussion.
Robert wrote: I believe that a plastic vapor barrier is an
invitation to problems in almost any thermal envelope. It was promulgated by
code when most houses were insulated with fiberglass and there was little
attention to (even recognition of) the need for
air-tightness.
Putting
a Vermont Residential Building Energy Standard (RBES/Code) required vapor
retarder with a perm rating of 1.0 or less on the warm-in-winter side of
nonframed ceilings, walls, and floors can and should be accomplished without the
use of poly. An appropriate vapor retarder can be installed via the use of
the airtight drywall approach (mentioned later in Robert's email) coupled
with the use of vapor retarder or barrier paints. This is a better
approach as poly almost never serves as an effective air barrier and in fact
usually interferes with efforts to achieve an effective air barrier. As
Robert also correctly implies later in his email, diffusion (water vapor
transport through permeable and semi-permeable building materials flowing from
areas of high vapor pressure to lower vapor pressure) is the minor vapor
transport mechanism. Air leakage following heat transfer (hot to cold)
is the major water vapor transporter in most buildings.
Robert
wrote:
The
same fiberglass-insulated house with 1" of exterior XPS and 0.35 ACH would
have an additional embodied energy payback of less than 1 year, in large part
because it results in much greater energy savings than the typical sprayed
urethane, mostly by eliminating thermal bridging.
If
the building assembly is such that "moisture or its freezing will not damage
building materials and/or insulation" (to quote RBES), as would be the case
with an exterior XPS wrap or some other exterior rigid foam insulation wrap
of sufficient R-value, the home would not require a warm-in-winter side vapor
retarder. I point out though that 2" XPS (R-10) or other
insulated sheathing materials at R-10 are needed in our climate zone to prevent
moisture or its freezing from damaging building materials and/or
insulation. At R-5, 1" XPS will allow condensing surfaces to exist
during sufficient portions of the year. With only an R-5 exterior
wrap, should warm moist interior air get into a wall cavity, it will find
surfaces below the dew point and condensation could then damage building
materials and/or insulation.
Robert wrote: I have calculated that, compared to a 2000 SF
reasonably well-sealed code-standard fiberglass-insulated house (0.5 ACH), a
urethane sprayed house (with insulated gable walls and roof assembly rather than
ceiling), even accounting for an increase in air-tightness (min. 0.35 ACH), will
have an additional embodied energy cost that would require 23 years of operation
to pay back.
The
ACH building tightness numbers Robert discusses refer to estimated "natural
air changes per hour" or ACHNatural (ACHNat). These numbers are
derived by testing the home with a blower door and then comparing the
leakage measured (CFM50 - cubic feet per minute at 50 pascals pressure
difference) to home's volume to estimate the air change rate that a house
leaks under "normal" conditions. This can only be roughly estimated and it
erroneously implies a specific air change rate as a constant. The air
change rate is not constant and varies widely over time because natural
ventilation is driven by temperature difference and pressure difference.
I
admit culpability in training many VT builders to look at and gauge their
performance via the ACHNat results they achieved on their Home Energy Rating
certificates. However, it would be far better if we looked at our
buildings using air changes per hour at 50 pascals pressure difference
(ACH50). This eliminates the estimate that has to be made as to what's
"normal" operation and significantly improves the accuracy of this
measurement. To determine ACH50 the following formula is used:
CFM50
x 60 (minutes/hour) / house volume (cu. ft.) = ACH50 (Air Changes per
Hour at 50 Pascals).
The
CFM50 and the house volume are outputs on the new Index Home Energy Rating
certificates. Target ACH50 results
should be <= 5 ACH50. Better yet
would be to eliminate the house volume and compare our leakage against the
amount of exterior surface area but we are not able to present that in our
certificates.
On
the last roughly 3,600 homes we have blower door tested (all participants in
Efficiency Vermont programs), 73% are at or below .35 ACHNat. For that
same sample, 69% are at or below 5 ACH50.
How
long do want our houses to last? I wouldn't sneeze at a 23 year payback if
we're looking at an economic life of 100+ years for the house.
Robert wrote: Open-cell sprayed Icynene has almost the same
embodied energy liability as the fiberglass, but it would result in a less
energy-efficient house.
Icynene
brand open-cell foam has a very similar R-value per inch of thickness as
fiberglass; however, the improved air tightness seen in most Icynene insulated
homes results in greater heating efficiency not less. We do generally see
spray-in-place insulated homes testing tighter than fiberglass batt
insulated homes and usually as tight as or tighter than cellulose insulated
homes.
Robert wrote: A similar house with 2x8 framing 24 oc (instead of
2x6 16 oc for the others), which uses no more total wood, and made very tight
with the air-tight-drywall system (0.25 ACH, which is adequate in a non-toxic
breathable house), would have 41% of the insulation embodied energy of the
fiberglass (less than 5% of the urethane) and use 39% less heating
energy.
My
comments here are that we can also build with 2"x 6" 24" oc and get better
performance. If we are to thicken the wall more we farther with a
minimum R-10 exterior insulation wrap to eliminate thermal bridging, lower
wetting potential, and enable drying to the inside by diffusion as we can now
legitimately eliminate the 1.0 perm vapor retarder. On top of that we can
achieve a whole wall R-value in the R-24 range (with fiberglass batts,
cellulose, or Icynene full cavity insulation, though wall performance will vary
based on the air sealing properties of the insulation, its installation
quality, and the effectiveness of the interior and exterior air barriers).
Houses don't breath. They should be built tight and ventilated with
equipment appropriate to maintain a consistent and appropriate air exchange
(when occupied) to control moisture levels, provide adequate fresh air, and
dilute indoor air contaminants of all sorts.
I
don't recommend spray-in-place foams as 1st choice for new construction because
we generally have sufficient building assembly thickness available and
cellulose is a preferred material for a multitude of reasons. However,
this is a right tool for right job issue. Spray-in-place foam does a great
job in insulating rim-band assemblies. It can be very useful when a sloped
ceiling constructed with scissors trusses exists that defies dense-packing with
cellulose. To my thinking spray-in-place foams are often the best tool
with existing homes where wall thicknesses are small and thickening them is not
feasible. I rebuilt much of my old farmhouse from the outside and
closed-cell foam was the only material that would effectively provide me with an
R-19.5 insulation, an air barrier, and a vapor barrier in a 3" cavity. It
is also the only reasonable solution for insulating and air sealing the old
field stone foundation.
----- Original Message -----From: [log in to unmask] href="mailto:[log in to unmask]">Robert RiversongTo: [log in to unmask] href="mailto:[log in to unmask]">[log in to unmask]Sent: Friday, December 12, 2008 11:04 AMSubject: Re: [VGBNTALK] damp cellulose
I believe that a plastic vapor barrier is an invitation to problems in almost any thermal envelope. It was promulgated by code when most houses were insulated with fiberglass and there was little attention to (even recognition of) the need for air-tightness.In addition to preventing a thermal assembly from breathing (diffusion drying to the inside), it also prevents a wonderfully hygroscopic material like cellulose from performing as a moisture buffer to stabilize indoor RH, and likely creates a static charge which draws negative ions out of the living environment.Now that it's been proven that, with reasonable indoor RH levels, diffusion contributes as little as 1% of the total moisture load in a thermal envelope during the heating season, and that stopping air movement is the key to preventing indoor-generated moisture problems in the structure, the air-tight drywall approach solves all the problems without creating more.Unfortunately, particularly for the sustainable building community, sprayed foam is being touted as a solution to moisture problems, when it (much like plastic VBs) creates its own set of negative consequences, since closed-cell foam has no moisture storage (buffering) ablity and open-cell foam can trap moisture and cause wood rot and mold. This, of course, in addition to the non-renewable resource depletion, embodied energy and carbon contribution issues.I have calculated that, compared to a 2000 SF reasonably well-sealed code-standard fiberglass-insulated house (0.5 ACH), a urethane sprayed house (with insulated gable walls and roof assembly rather than ceiling), even accounting for an increase in air-tightness (min. 0.35 ACH), will have an additional embodied energy cost that would require 23 years of operation to pay back.The same fiberglass-insulated house with 1" of exterior XPS and 0.35 ACH would have an additional embodied energy payback of less than 1 year, in large part because it results in much greater energy savings than the typical sprayed urethane, mostly by eliminating thermal bridging.Open-cell sprayed Icynene has almost the same embodied energy liability as the fiberglass, but it would result in a less energy-efficient house.A similar house with 2x8 framing 24 oc (instead of 2x6 16 oc for the others), which uses no more total wood, and made very tight with the air-tight-drywall system (0.25 ACH, which is adequate in a non-toxic breathable house), would have 41% of the insulation embodied energy of the fiberglass (less than 5% of the urethane) and use 39% less heating energy.
--- On Fri, 12/12/08, Tim Yandow <[log in to unmask]> wrote:I have found that using a vapor barrier with wet spray is an invitation to disaster though. The walls need to breathe. Tim Yandow